UPS (Uninterruptable Power Supply) What Size / How Long
You are asked from the end user what kind of UPS they need. What are you going to answer? The answer is here. We simulated based on our DVR with our camera for the customer, who wants to know size of UPS and running time (How long UPS can take care of power when power outage)
Case Study (TM 16 Elite+ with 8 of SENS cameras)
TM 16 Elite + with 1HDD, CD/RW : 0.35 – 0.4 Amp / 115 Volt
SENS Camera : 0.12 – 0.2 Amp / 115 Volt
Total VA= 115 * (0.4+(0.2*8)) = 230 VA (He need about 300 – 350VA at least)
If customer uses APC Back UPS Pro 650 Model, he will get about 18 min (Run Time) roughly (see the below table “Run Capacity”
Run capacity is totally depending on the manufacturer table (Here, APC) Most of their website shows “run capacity” table.
If UPS size named by Watt (W) not by (VA), you need to consider PF (Power Factor), usually real watt is less than VA because of PF (Normal PF is 60%)
W = VA x PFhttp://www.pcguide.com/ref/power/ext/up ... ity-c.html As discussed in the section on UPS capacity and run time (which you should read and understand before reading this page) a UPS has a limit on the loads it can power. In fact, it has two limits: a maximum apparent power load specification (in VA) and a maximum actual power load specification (in W). Sometimes the actual power load limit is not explicitly provided but must be computed. If the wattage is not listed specifically, it is safe to assume that it is 60% of the VA number. However, you should read the specifications carefully, because some UPSes use a different ratio.
The rule for sizing a UPS is simple in concept, and difficult in application: the loads you attach to the UPS cannot exceed either of its limits. Let's use a couple of examples to see how the two limits work: Let's say we have a 650 VA UPS. The wattage limit is not specified, so to be safe, we use 60%, which yields a limit of 390W. This means any load we run cannot exceed either 650 VA or 390 W. Some sample power supply loads:
• Regular Power Supply, 500 VA Rating: A regular power supply with a rating of 500 VA will run fine on this UPS, because its power factor is probably about 60%, much as the UPS manufacturer assumed (but you should check its specifications, if you can.). Even if the power factor is 70%, that's still 350 W, under the UPS's limit.
• Power-Factor-Corrected Power Supply, 500 VA Rating: Some power supplies have circuitry added to them that corrects the power factor to approximately 100% (sometimes called power factor 1). In this case the power supply will have a 500 VA rating and also a 500 W rating. This power supply will overload the UPS we are discussing here because its W rating is too high.
Now that we understand what the limits are on the UPS side, let's take a look at the load side. To figure out what a load will demand of the UPS, we need to know both its VA and W ratings. Unfortunately, many manufacturers do not provide the information required to make a knowledgeable decision. An upper bound of the VA requirements of a unit can be obtained by looking for its current rating, which almost all devices have on a label or plaque near their power cord. However, these numbers are usually rather conservative. If a device has a 2A rating, then its nominal VA requirement is 2*115=230 VA. However, in practice, it may never actually require more than, say, 175 VA. There's no way to know for sure unless you know how to test the device electrically, so if you want to be absolutely certain, you must be conservative and use the maximum figure of 230.
PC power supplies introduce an added level of confusion. :^) When people talk about power supplies, they usually say something like "that's a 300 watt power supply". It's important to realize that the number "300" in that designation is the approximate, total output DC power of the power supply. That number is absolutely meaningless when it comes to sizing a UPS! It doesn't represent either the VA or W requirements of the supply. Most power supplies will have a current specification that you can use to calculate the VA maximum of the supply as in the previous paragraph, but if you use this you will probably over-purchase your UPS, because the output rating of the power supply is itself a maximum and only represents what will be required if the power supply is completely maxed-out. A 300 W power supply on a typical PC isn't actually putting out anywhere near that total. See here for more details.
Fine, fine, so now I have told you everything you shouldn't do to size a UPS. What are you actually supposed to do? Unfortunately, ideally sizing a UPS isn't easy to do. You often have to be conservative with your numbers and purchase a bit more UPS than you really need, to make sure you have your bases covered. Here are some tools and techniques you can use to help you with sizing:
• Use A Sizing Tool: American Power Conversion has a useful UPS sizing tool on its web site. Other companies also offer sizing programs. These tools are specifically geared towards UPS sizing, and have databases of typical real VA and W requirements of various devices. They are probably the best place to start.
• Read the Recommendations: For a UPS you are considering, look at the recommendations the manufacturer makes for the unit. Compare them to what you are going to run and use common sense. If the manufacturer's crack marketing team says "ideal for small desktop PCs" and you are running a high-powered dual-processor graphics workstation, you are probably asking for trouble if you try to run it on that UPS.
• Test the UPS: The absolute best way to size a UPS, if you can do it, is to test it. If you have a friend with a UPS of approximately the same size as one you need, borrow it, fully charge the battery, plug in your system, and power it up. Then pull the plug on the UPS and see how long the power lasts before the UPS shuts down. (Obviously, don't do this with important data files open etc.) If the UPS works properly and lets you close down and save your work, you know you are protected.
• Be Conservative: A little too much is better than a little too little when it comes to a UPS.
Once you know your UPS has enough capacity to meet the requirements of your hardware, the next matter is one of run time: how much do you need? The most important goal of a UPS is to provide enough power to let you gracefully shut down your system; anything beyond that is "gravy", so to speak, that lets you keep working through an outage for a while. To get enough run time to actually work through anything but the shortest blackouts, you will usually have to pay substantially more money. To lengthen your run time, don't plug unnecessary gadgets into your UPS's backed-up receptacles. For example, most peripherals don't need to be plugged into a UPS. Most UPS manufacturers provide charts that show theoretical run-time for various sizes of load, such as the one shown on this page.
One item that you should consider having plugged into your UPS is your monitor. Having the monitor shut off suddenly in a blackout won't cause loss of data, for example, so it isn't mandatory to have it connected. However, if you have a blackout and your PC stays up but your monitor goes down, how are you going to see what you are doing when you try to save your data and shut down your applications? :^) Monitors, particularly those with large CRTs, can draw a substantial amount of power, so keep this in mind when doing your sizing.
http://www.pcguide.com/ref/power/ext/up ... ity-c.htmlCapacity and Run Time
One of the most important features of a UPS is its capacity. Another is its run time. While these two concepts are related, they are not the same. It's important to understand the difference between them, as these numbers play a critical role in UPS sizing.
The run time that a UPS provides is the number of minutes that the UPS will be able to provide power from the battery for a given load level. Since driving more equipment requires more power to be taken from the battery, driving more load will result in shorter run time. A UPS with a larger battery, or with an add-on battery pack, will provide longer run time for a given load size. Run time is critically important because it tells you how long a power outage the UPS can handle before the battery runs out. Most UPS manufacturers will provide tables that show the typical run times for a model based on the loads it has to handle. Here's a sample table for an APC Back-UPS Pro 650 model:
Load (VA) Run Time (minutes)
100 49
200 22
300 14
400 9.3
500 7.2
600 5.8
In the chart I have highlighted the run time values for 100, 200 and 400 VA. Notice that when you double the load, the run time is reduced not by half, but by more than half. One key reason for this is that lead-acid batteries discharge more quickly when they are drawing more load. See the discussion of the UPS battery for a thorough explanation of battery capacity and the effect of discharge rate.
After looking at that chart, a natural question might be: "If it will run a 200 VA load for 22 minutes, and a 400 VA for 9.3 minutes, how long will it run an 800 VA load for? 4 minutes? 2 minutes?" Unfortunately, the answer to this is probably "0 minutes". This is where capacity enters into the picture. The UPS has a nominal maximum capacity, usually indicated by the number in its model name. In this example, it is 650 VA. The UPS will probably handle a load slightly above this figure--much the way your car doesn't stop dead when the fuel gauge hits "E"--but going to 800 VA will probably cause the UPS to overload and shutdown when it goes on battery. The reason for a maximum capacity figure is not just the batteries. It is also a function of the ability of the UPS's circuitry and even its wires to handle a particular size of load. It's also a safety issue, as exceeding the current limit of a circuit is unsafe.
While the UPS's capacity is rated in terms of its nominal load limit in, there is another limit that must be observed. To understand this other limit we must understand the difference between apparent power, which is the power provided as input to a device, and actual power, which is the power the device actually uses. For most complex devices, these are not the same. The ratio of actual power to apparent power of a device is its power factor. For PC power supplies it is often around 60%. (These concepts are explained in this Power Basics section.) The load on a UPS cannot exceed its apparent power load limit in VA, nor can the load exceed its actual power load limit in Watts. Many UPS manufacturers do not publish a specific wattage limit, but instead assume that the power factor of its loads will be about 60%. If you are driving a load that has a power factor of 60%, then the apparent and actual power limits are the same. But if the loads you are driving have a power factor higher than 60%, you cannot use the total VA limit because your watt usage will be over the wattage limit. If all this seems a bit confusing, you're probably right. I explain further, with examples, in the section on UPS sizing.
Many larger UPS models offer the ability to increase run time by adding on expansion battery packs. These expandable units are great, especially if you aren't sure of your exact load requirements when you purchase the unit. Expanding the UPS saves money over buying another since you are only paying for extra battery and not duplicating the UPS's other components.
Next: Sizing